1. 20 amp breaker wont activate. 2. Other side of the break is for the converter, 20 amp, working ok 3. Yellow power cable to AC unit control box has no power (Black, White & Green wires in the yellow cable) 4. No loose or burnt wires in the breaker box, the AC unit control box or the thermostat 5. Fuses in thermostat and breaker box ok. Battery volts in breaker box 13.5 volts
Anyone know where the power source for the yellow cable is located? Any ideas and opinions are welcome.
Thank you for your time. Appreciate it.
|
|
cloud
Weekender RV’er
Posts: 54
|
Post by cloud on Nov 5, 2018 21:40:09 GMT -5
Not sure what you mean when breaker won't activate. In power distribution panel there should be a breaker marked rear ac. Is power coming out of the breaker?
|
|
|
Post by Edd505 on Nov 5, 2018 22:21:14 GMT -5
Check for power from the breaker and check for loose wire on the backside of that breaker. While your back there check all to insure they have not worked loose.
|
|
rickeys
Newbie RV’er
Durango Gold 384RLT in Delaware
Posts: 17
|
Post by rickeys on Nov 6, 2018 5:57:35 GMT -5
if you have two a/c's then you more than likely have 50 amp service, just asking are you using an adapter to 30 amp? If so that may be the issue.
|
|
|
Post by Edd505 on Nov 6, 2018 14:08:38 GMT -5
if you have two a/c's then you more than likely have 50 amp service, just asking are you using an adapter to 30 amp? If so that may be the issue. 30 will run 1 A/C adding the second trips the breaker so Zero A/C
|
|